    The plumber ran a pvc sch. 40 waste line about 1/4" away from a 1 1/4" iron monoflow loop heating pipe which feeds hot water baseboards. This near contact point occurs at a 90 degree bend, so if I push the two pipes together, there is only contact at that point as opposed the two two pipes running parallel. I expect the water temperature will be about 180 degrees in the heating pipe. Will there be a problem with the pvc melting or becoming brittle from the heat? I could not find anything on line about this and plumber says its fine.

  • #2
    Re: Melting temperature of PVC

    It's rated for 140 degree water.

    I can't say for sure that your scenario is OK, but I'd wrap the pvc loosely(leave what ever air gap possible) w/ some light gauge aluminum or that shiny pipe wrap and I wouldn't lose sleep.

    Comment


    • #3
      Re: Melting temperature of PVC

      That's what I was looking to hear. I have enough room to get a little insulation in between the two. I will give that a shot.

      Comment


      • #4
        Re: Melting temperature of PVC

        The continuous service temperature limit for PVC is 160 degrees F. Max deflection temp is 154 degrees F. PVC is not rated for hot water service. The melting point is 360 degrees F.

        Since this is a drain line and not under any pressure, there should be no problem as long as you take the suggestion to insulate the area around the potential point of contact.

        Comment


        • #5
          Re: Melting temperature of PVC

          Physical Properties of PVC Pipe Value Test Method
          GENERAL
          Cell Classification 12454 ASTM D1784
          Maximum Service Temperature 140°F
          Color white, dark gray
          Water Absorption % increase 24hrs @ 25°C .05 ASTM D570
          Hardness, Rockwell 110-120 ASTM D785
          Poisson's Ratio @ 73°F .410
          Hazen-Williams Factor C=150
          MECHANICAL
          Specific Gravity (g/cu,cm) 1.40 ± .02 ASTM D792
          Tensile Strength, psi @ 73°F 7,450 ASTM D638
          Modulus of Elasticity, psi @ 73°F (Tensile Modulus) 420,000 ASTM D638
          Flexural Strength, psi @ 73°F 14,450 ASTM D790
          Compressive Strength, psi @ 73°F 9,600 ASTM D695
          Izod Impact, ft-lb./in. @ 73°F .75 ASTM D256
          THERMAL
          Coefficient of Linear Expansion (in/in/°F) 2.9 x 10 (to -5) ASTM D696
          Coefficient of Thermal Conductivity (BTU/in/hr/ft/°F) 3.5 ASTM C177
          Heat Distortion Temperature, °F @ 264 psi 170 ASTM D648
          Specific Heat, Cal/°C/gm .25 ASTM D2766
          ELECTRICAL
          Dielectric Strength, V/mil 1,413 ASTM D149
          Dielectric Constant, 60 Hz, 30°F 3.7 ASTM D150
          Volume Resistivity, ohm/cm @ 95°C, ohms/cm 1.2 x 10 (to 12) ASTM D257
          Harvel PVC Pipe is non-electrolytic
          FLAMMABILITY
          Flammability Rating V-0 UL 94
          Flame Spread Index <10 ASTM E162
          Flame Spread 0-25 10-25 ULC ASTM E84
          Flash Ignition Temp 730°F
          Average Time of Burning (sec.) <5 ASTM D635
          Average Extent of Burning (mm) <10
          Burning Rate (in/min) Self Extinguishing
          Softening Starts, (approx.) 250°F
          Material Becomes Viscous 350°F
          Material Carbonizes 425°F
          Smoke Generation 80-225 600-1000 ULC ASTM E84

          Comment


          • #6
            Re: Melting temperature of PVC

            I would take a piece of Hardy board tile undelayment and put between the two pipes. That would insulate it fully. this is the 1/4 gypsum tile undelayment material. I may be calling it by the wrong name.

            Kirk

            Comment


            • #7
              Re: Melting temperature of PVC

              KG,

              That's a good idea