Condo remodel:
*100amp service
*208 voltage (getting 205 in the apt. confirmed by 2 probes).
*#6 wire(maybe a 20 foot run)
*60amp breaker for a unit that is speced for 54amps
This TWH will only fully heat the water when we damper back the water supply to say 50%. otherwise water is luke warm at best.
When calling for hot water this 208v unit is drawing 47 to 48 amps. With all equipment in the appartment running together the draw on the appartment is 91 to 95 amps. No perceptable voltage drop during the time we metered the appartment. All equipment is in good working order. I have been recommending these units to customers and have been trouble free for all five other installs. My electrician does not know what to make of it. My Plumber can only recommend that all the air is perged from the supply lines. Did that. This unit is speced to handle 3psi all the way to 150psi. I d seriously do not think I have more than 100psi in this appartment.
Any thoughts on why this unit is not heating properly (its the second one from the manufacturer). The manufacturer also is stumped.
*100amp service
*208 voltage (getting 205 in the apt. confirmed by 2 probes).
*#6 wire(maybe a 20 foot run)
*60amp breaker for a unit that is speced for 54amps
This TWH will only fully heat the water when we damper back the water supply to say 50%. otherwise water is luke warm at best.
When calling for hot water this 208v unit is drawing 47 to 48 amps. With all equipment in the appartment running together the draw on the appartment is 91 to 95 amps. No perceptable voltage drop during the time we metered the appartment. All equipment is in good working order. I have been recommending these units to customers and have been trouble free for all five other installs. My electrician does not know what to make of it. My Plumber can only recommend that all the air is perged from the supply lines. Did that. This unit is speced to handle 3psi all the way to 150psi. I d seriously do not think I have more than 100psi in this appartment.
Any thoughts on why this unit is not heating properly (its the second one from the manufacturer). The manufacturer also is stumped.