I'm having my house siding redone, and having soffit vents installed in the existing, unvented soffits. The contractor is planning on cutting a 2" continuous vent in the existing soffit, and I'll then have Certainteed 3 1/3" Invisivent installed on top so it looks much nicer. I have a 1,260 sq. ft. attic, so need 605 sq. in of intake and exhaust venting according to the 1/150 rule. Per the Invisivent literature, there is approximately 10 sq. in of net free area/sq. ft. I'm having about 80 feet of Invisivent installed, soffit is about a foot wide, so approx. 80 sq. ft. That would give me 800 sq. in of net free area for the intake, more than enough. My concern is that I won't get anywhere near this number with only a 2" continuous vent cut into the existing soffit. We will not be installing anything in the continuous soffit, it will just be cut into the existing and covered with the Invisivent. Is there any calculation to try to determine how much intake I may get? The 2" continuous would be a little over 2,000 sq. in of intake (80' of soffit * 2 in). I have a 40' ridge vent already installed, although it's the cheaper mesh type. I'm concerned the ventilation won't be balanced or work efficiently. My attic is typically 40-50 degrees hotter than outside, and I was really hoping adding the soffit vents would help to lower this considerably. Thanks for any and all input and advice.