Insulating existing garage floor
I am converting a garage floor into a bedroom in central MA.
The uninsulated slab is 8" below finished wood floor. Am going to carpet the new floor. Am I best off with 2x8 sleepers and rockwool insulation or just 2" rigid foam with 3/4" plywood tapconned into slab?
The HO is fine with having a step at the threshold.
I understand that IECC calls for more than R10 in Zone 5, but wondering
if the overall assembly would be better with rigid board.
Thanks,
CDQuality is not expensive.. it's priceless.
-
01-05-2013, 06:32 AM #2
Veteran Contributor
- Join Date
- Oct 2006
- Location
- Greensboro, NC
- Posts
- 1,384
Re: Insulating existing garage floor
-
01-05-2013, 11:47 AM #3
Veteran Contributor
- Join Date
- Jul 2007
- Location
- Toronto, Ontario, Canada
- Posts
- 801
Re: Insulating existing garage floor
The foam provides a complete capillary break and, by eliminating thermal bridging of the sleepers, provides a higher effective R Value for the floor than by using sleepers.
Last edited by worthy; 01-05-2013 at 11:57 AM.
"there is no good war, and no bad peace."
Benjamin Franklin
-
01-05-2013, 12:28 PM #4
Veteran Contributor
- Join Date
- Jul 2006
- Location
- Portland, OR
- Posts
- 2,315
Re: Insulating existing garage floor
6" foam, 2x4's on flat, 1/2" plywood. Flat, aligned, warm, and easy.
-
01-05-2013, 04:05 PM #5
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,508
-
01-05-2013, 04:20 PM #6
Veteran Contributor
- Join Date
- Sep 2009
- Location
- Portland, Maine
- Posts
- 1,199
Re: Insulating existing garage floor
If 8" is the build-up....6" foam, 2" concrete with radiant.
Last edited by Dutchman; 01-05-2013 at 04:20 PM. Reason: math error
Portland Renovations, Inc.
www.portlandrenovations.com
-
01-05-2013, 05:07 PM #7
Veteran Contributor
- Join Date
- Jul 2006
- Location
- Portland, OR
- Posts
- 2,315
Re: Insulating existing garage floor
#5, well, you have to get a proper density of foam.
#6, I like that better than the wood assembly. And since there's probably a slope to the garage floor, concrete topping can compensate. Although I might go for 2-1/2" min. on the concrete
-
01-05-2013, 08:38 PM #8
New Member
- Join Date
- Sep 2008
- Location
- Boston, MA
- Posts
- 14
Re: Insulating existing garage floor
this is a lower end rental unit, so I think I'm going to skip the 2" concrete topping with radiant.
Does double plywood need to be tapconned to floor, or can it float? Do sleepers need to be tapconned if used with single plywood system?Quality is not expensive.. it's priceless.
-
01-06-2013, 07:09 AM #9
Veteran Contributor
- Join Date
- Sep 2009
- Location
- Portland, Maine
- Posts
- 1,199
Re: Insulating existing garage floor
Does skipping the radiant help the budget?
Any wood assembly is going to be a bit hollow sounding.
So, from bottom up: 6 mil poly, foam, sleepers @ 12" o.c., 3/4" ply. Let the sleepers and ply float on the foam.Portland Renovations, Inc.
www.portlandrenovations.com
-
01-06-2013, 02:55 PM #10
Veteran Contributor
- Join Date
- Jul 2007
- Location
- Toronto, Ontario, Canada
- Posts
- 801
Re: Insulating existing garage floor
I fail to see the purpose of the sleepers or of the poly, which will just trap moisture between the concrete and the poly; nor the need for R30.
An alternative approach designed for a monolithic slab is in Lstibruek's Builder's Guide to Cold Climates p. 107: dimpled plastic sheet (such as Delta FL) XPS with no facers and 3/4" t&g plywood not fastened "so that gas barrier/air barrier is not compromised". Also, Lstiburek notes that in this type of construction insulation should be limited so that the slab can dry upwards.
Elsewhere Lstiburek shows a layering Figure 3--of XPS, building paper and wood subfloor.Last edited by worthy; 01-06-2013 at 04:57 PM.
"there is no good war, and no bad peace."