Thread: Backup generators
-
09-28-2012, 03:38 PM #1
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,500
Backup generators
For those of you who do generators routinely:
What line of generators do you like for a larger house? Need to look at some options for a large house with two 200A panels. We'll be looking at backing up the whole house and (maybe) just reshuffling the panels so we back up one panel only.
Too many products out there, need to narrow it down to a couple of solid manufacturers with good price/performance.
-
09-28-2012, 05:18 PM #2
Custom Home Builder
- Join Date
- Jun 2004
- Location
- Houston & Washington Texas
- Posts
- 11,377
Re: Backup generators
We are currently installing a 60KW generator Kohler in one house almost completed and a 20KW Generac in another house just completed . My vendor (below) tells me the Kohler is a better unit.
http://www.generatorsofhouston.com/index.php
-
09-28-2012, 06:20 PM #3
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,500
Re: Backup generators
Thanks Allan. We're probably looking in the 20-40kW range.
Edit: Allan, do you pour concrete pads for your generators or use their plastic bases? Some manufacturers (Kohler included) suggest the built-in plastic base is adequate, but I'm a little skeptical.Last edited by dgbldr; 09-28-2012 at 06:27 PM.
-
09-28-2012, 07:02 PM #4
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Bellbrook. Ohio
- Posts
- 1,662
Re: Backup generators
We use Kohler generators - we are getting asked more and more about them.
We always pour a pad - the specs dictate the size and there is typically an opening in the slab to bring up the gas line and take out the electrical lines.-Dan
-
09-28-2012, 07:11 PM #5
Custom Home Builder
- Join Date
- Jun 2004
- Location
- Houston & Washington Texas
- Posts
- 11,377
Re: Backup generators
There is a fairly high end 'hood I build in that also has setback and sound restrictions for generators. (By the way, Bush I lives here).
http://tanglewoodhomes.org/wp-conten...tor-Policy.pdf
-
09-28-2012, 08:23 PM #6
Veteran Contributor
- Join Date
- Feb 2008
- Location
- Northwest Indiana
- Posts
- 5,578
Re: Backup generators
dg,
I get mine from Ziller, they're in your neck of the woods;
http://www.zillerelectric.com/
I install the Generac 20k (actually 17k on natural gas), with their load shedding switch.
The Generacs have a built-in pad.
TomLast edited by tjbnwi; 09-28-2012 at 09:57 PM.
-
09-29-2012, 12:42 AM #7
Veteran Contributor
- Join Date
- Apr 2006
- Posts
- 151
Re: Backup generators
For residential size generators you basicly got two choices- Kholer and Generac. I would pick the one most available. Here it is Generac.
I would always recommend a concrete pad and let the owner decide.
-
09-29-2012, 02:56 PM #8
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,500
Re: Backup generators
Tom, are you using the gens with the little 2 cyl air cooled engines? Never used those. How do they perform? Are they loud? Big step in price from those to the water cooled GM I4 and V6 engines.
-
09-29-2012, 07:33 PM #9
Veteran Contributor
- Join Date
- Feb 2008
- Location
- Northwest Indiana
- Posts
- 5,578
Re: Backup generators
Yep, 2 cylinder air cooled. According to Generac, they manufacture their own engines for the generators.
No issues with the engines, Generac did have a run of bad LCD panels. Problem has been corrected and they cover them under warranty for up to 3 years. I have heard Kohler had some main breaker issues on their 20k units. To the best of my knowledge that has been corrected also.
Fairly easy to install. Most important thing is gas supply. All so far have needed a higher capacity meter. One needed a new line, quote from utility was 20k to upgrade the line. You will need a gas pressure gauge to do the final adjustments.
They are louder than a central AC unit. I believe Ziller has the db listed.
Don't forget you most likely will need a permit.
I want to try the vertical GE. Just because. Also Generac makes a lot of rebadges, Honeywell comes to mind. Execpt for color, they are exactly the same.
TomLast edited by tjbnwi; 09-29-2012 at 07:36 PM.
-
09-29-2012, 08:58 PM #10
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,500
Re: Backup generators
Yes in most jurisdictions I need 3 permits, not one. Building permit, for placement, easements, noise, etc. Then electrical and gas piping.
-
09-29-2012, 09:24 PM #11
Veteran Contributor
- Join Date
- Feb 2008
- Location
- Northwest Indiana
- Posts
- 5,578
Re: Backup generators
Our permits come on one page with the apporperate boxes checked.
Make certian you use the flex gas hose supplied with the generator. It connects hard pipe to regulator. I've seen a snapped regulator due to it not being used.
You should also sell a service contract with the sale of the generator. Someone has to change the oil and service the battery.
I set them to test run once a week, they report back to a module in the home. I had one report a clogged air filter after 4 15 minute test runs. It was a software glitch, Generac updated the software remotely.
Tom
-
10-02-2012, 06:16 AM #12
Custom Home Builder
- Join Date
- Jun 2004
- Location
- Houston & Washington Texas
- Posts
- 11,377
-
10-05-2012, 07:42 PM #13
Veteran Contributor
- Join Date
- Feb 2008
- Location
- Northwest Indiana
- Posts
- 5,578
Re: Backup generators
dg,
This is an install that we had to reshape the landscaping on. The rock provides good drainage around the unit.
This is a 20k on natural gas, so 17k. It came from Ziller.
(Someday I'll learn to take better photos)
Tom
-
11-04-2012, 01:59 PM #14
New Member
- Join Date
- Nov 2012
- Posts
- 1
Re: Backup generators
Hi Forum,
Newbie (to the forum) here. Renovating a house in Jersey which includes installing a 14kW Generac generator. My HVAC contractor suggests using the Nexus controller which provides load shedding capability - he claims this protects the HVAC equipment which will be hooked up to the generator. My electrician and I were only planning on using the standard transfer switch.
Thoughts? Opionions? Thanks!
-
11-04-2012, 03:12 PM #15
Veteran Contributor
- Join Date
- Feb 2008
- Location
- Northwest Indiana
- Posts
- 5,578
Re: Backup generators
Put in a 20 if there is a concern for overload. Your 14 is only 13 on NG.
How many AC condensers? What tonnage? Natural gas, LP, electric furnace?
POCO service amperage?
I would shed the AC condenser, not the furnace.
What are the HVAC contractors concerns?
TomLast edited by tjbnwi; 11-04-2012 at 03:19 PM.