    I am a Code Inspector and am concerned about a typical treatment of thruwall flashing in the South East on wood frame residential construction.

    The typical location of the flashing appears to leave the bottom of the sheathing and the bottom plate exposed to moisture build up and rot.

    The flashing is typically taken to the inside face of the stud wall. As a result it leaves a potential gap at the bottom of the housewrap, where any moisture flowing down the housewrap can wick in

    This could be prevented if the flashing were taken up under the housewrap against the front face of the sheathing, lapping it by at least 6”.

    A brick veneer wall is already vulnerable to moisture intrusion, and the bottom of the cavity is typically full of mortar droppings impeding drainage. Additionally the use of 6 mil poly for flashing is, of course, cause for concern, but code does not disapprove this.

    To compound the problem, the nailing of sheathing to the bottom plate is critical in high wind areas to securing the building for shear and uplift. If this sheathing stays wet, the nails loose their strength, and eventually moisture migrates inside.

    Does anyone know any reasons why the flashing is taken to the inside face of the studwork?

    Does anyone see problems with requiring it be brought to the face and lapped with houserap ?
    Attached Files Attached Files

  2. #2
    Join Date
    Jul 2007
    Location
    Northern Jersey
    Posts
    1,283

    Default Re: Brick Veneer Flashing

    I would rather see that flashing at the face of the wall under the WRB myself. Perhaps that isnt polyethylene but was meant to be flashing tape. Im no mason either but I believe pea gravel is supposed to fill the cavity base to allow drainage in case of mortar build up. They also make a felt.
    Tom

  3. #3
    Join Date
    Jun 2004
    Location
    Des Moines, Iowa
    Posts
    3,861

    Default Re: Brick Veneer Flashing

    Here is a great guide to some of the details
    http://www.olympiancares.com/mason%2...k%20veneer.pdf
    Mark Parlee
    BESI(building envelope science institute) Envelope Inspector
    EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
    Level one thermagrapher (Snell Training)
    www.thebuildingconsultant.com
    www.parleebuilders.com
    You build to code, code is the minimum to pass this test. Congratulations your grade is a D-

  4. #4
    Join Date
    Sep 2005
    Location
    west milford n.j.
    Posts
    892

    Default Re: Brick Veneer Flashing

    thanks Mark,not a mason but nice to get a heads up on the masonry to siding transitions
    Tom

  5. #5
    Join Date
    Jun 2004
    Location
    Des Moines, Iowa
    Posts
    3,861

    Default Re: Brick Veneer Flashing

    Tom
    It is a well written document; amazing how many do not follow anything close.
    Mark Parlee
    BESI(building envelope science institute) Envelope Inspector
    EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
    Level one thermagrapher (Snell Training)
    www.thebuildingconsultant.com
    www.parleebuilders.com
    You build to code, code is the minimum to pass this test. Congratulations your grade is a D-

  6. #6

    Default Re: Brick Veneer Flashing

    Appreciate people's input. My questions remain:

    Does anyone know any reasons why the flashing is taken to the inside face of the studwork?

    Does anyone see problems with requiring it be brought to the face of the sheathing and lapped with housewrap ?

    Nick Coulson

  7. #7
    Join Date
    Sep 2005
    Location
    west milford n.j.
    Posts
    892

    Default Re: Brick Veneer Flashing

    seems like the ''rubber boot'' scenario waiting to happen
    Tom

  8. #8
    Join Date
    Jun 2004
    Location
    Des Moines, Iowa
    Posts
    3,861

    Default Re: Brick Veneer Flashing

    Nick
    I do not see why you would take it to the inside.

    I think the face of the sheathing with the lap is the way to go
    Mark Parlee
    BESI(building envelope science institute) Envelope Inspector
    EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
    Level one thermagrapher (Snell Training)
    www.thebuildingconsultant.com
    www.parleebuilders.com
    You build to code, code is the minimum to pass this test. Congratulations your grade is a D-

  9. #9
    Join Date
    Jul 2007
    Location
    Northern Jersey
    Posts
    1,283

    Default Re: Brick Veneer Flashing

    Quote Originally Posted by ncoulson View Post
    Appreciate people's input. My questions remain:

    Does anyone know any reasons why the flashing is taken to the inside face of the studwork?

    Does anyone see problems with requiring it be brought to the face of the sheathing and lapped with housewrap ?

    Nick Coulson
    The intent of the code is to prevent water from entering the wall cavity. I believe the detail in your picture is wrong, the designer could have made a mistake.
    Tom

  10. #10
    Join Date
    Jul 2006
    Location
    Portland, OR
    Posts
    2,467

    Default Re: Brick Veneer Flashing

    We had another thread here on the same thing, except without the brick ledge. All were flabergasted. It just seems to be SE tradition. Who knows how these things get started

    The plastic in your detail serves no purpose, really, and the only drawback is absence of bonding between the bottom course of brick and the foundation. Bottom of the sheathing only gets wet if the WRB is short - and that's a WRB problem, not a plastic problem.

    With a 2-brick ledge, all one needs to do is extend the WRB over the face of the back face of the ledge, and one is good.

    If there is no brick ledge THEN one needs a good stick-on membrane and/or sheet metal flashing all around the base. That's how its done around here. We spend the money on metal, not on the concrete forming. Go figure

  11. #11
    Join Date
    Jul 2007
    Location
    Northern Jersey
    Posts
    1,283

    Default Re: Brick Veneer Flashing

    I remember that thread NW but not the detail, I think its was Pete Engle who referred to the flashing detail as a "row lock" in where the brick is not bonded to the masonry cap. I still find that odd, according to that explanation the brick rested on a copper flashing with-in a mortar joint by gravity. That doesn't seems right to me.
    Tom

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts