Thread: Brick Veneer Flashing
-
03-08-2010, 02:49 PM #1
New Member
- Join Date
- Mar 2010
- Posts
- 2
Brick Veneer Flashing
Brick Veneer Flashing
I am a Code Inspector and am concerned about a typical treatment of thruwall flashing in the South East on wood frame residential construction.
The typical location of the flashing appears to leave the bottom of the sheathing and the bottom plate exposed to moisture build up and rot.
The flashing is typically taken to the inside face of the stud wall. As a result it leaves a potential gap at the bottom of the housewrap, where any moisture flowing down the housewrap can wick in
This could be prevented if the flashing were taken up under the housewrap against the front face of the sheathing, lapping it by at least 6”.
A brick veneer wall is already vulnerable to moisture intrusion, and the bottom of the cavity is typically full of mortar droppings impeding drainage. Additionally the use of 6 mil poly for flashing is, of course, cause for concern, but code does not disapprove this.
To compound the problem, the nailing of sheathing to the bottom plate is critical in high wind areas to securing the building for shear and uplift. If this sheathing stays wet, the nails loose their strength, and eventually moisture migrates inside.
Does anyone know any reasons why the flashing is taken to the inside face of the studwork?
Does anyone see problems with requiring it be brought to the face and lapped with houserap ?
-
03-08-2010, 04:31 PM #2
Veteran Contributor
- Join Date
- Jul 2007
- Location
- Northern Jersey
- Posts
- 1,088
Re: Brick Veneer Flashing
I would rather see that flashing at the face of the wall under the WRB myself. Perhaps that isnt polyethylene but was meant to be flashing tape. Im no mason either but I believe pea gravel is supposed to fill the cavity base to allow drainage in case of mortar build up. They also make a felt.
Tom
-
03-09-2010, 09:59 PM #3
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Des Moines, Iowa
- Posts
- 3,636
Re: Brick Veneer Flashing
Here is a great guide to some of the details
http://www.olympiancares.com/mason%2...k%20veneer.pdfMark Parlee
EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
Level one thermagrapher (Snell Training)
www.thebuildingconsultant.com
www.parleebuilders.com
You build to code, code is the minimum to pass this test. Congratulations your grade is a D-
-
03-09-2010, 10:34 PM #4
Veteran Contributor
- Join Date
- Sep 2005
- Location
- west milford n.j.
- Posts
- 892
Re: Brick Veneer Flashing
thanks Mark,not a mason but nice to get a heads up on the masonry to siding transitions
Tom
-
03-09-2010, 11:10 PM #5
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Des Moines, Iowa
- Posts
- 3,636
Re: Brick Veneer Flashing
Tom
It is a well written document; amazing how many do not follow anything close.Mark Parlee
EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
Level one thermagrapher (Snell Training)
www.thebuildingconsultant.com
www.parleebuilders.com
You build to code, code is the minimum to pass this test. Congratulations your grade is a D-
-
03-10-2010, 10:49 AM #6
New Member
- Join Date
- Mar 2010
- Posts
- 2
Re: Brick Veneer Flashing
Appreciate people's input. My questions remain:
Does anyone know any reasons why the flashing is taken to the inside face of the studwork?
Does anyone see problems with requiring it be brought to the face of the sheathing and lapped with housewrap ?
Nick Coulson
-
03-10-2010, 11:24 AM #7
Veteran Contributor
- Join Date
- Sep 2005
- Location
- west milford n.j.
- Posts
- 892
Re: Brick Veneer Flashing
seems like the ''rubber boot'' scenario waiting to happen
Tom
-
03-10-2010, 01:08 PM #8
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Des Moines, Iowa
- Posts
- 3,636
Re: Brick Veneer Flashing
Nick
I do not see why you would take it to the inside.
I think the face of the sheathing with the lap is the way to goMark Parlee
EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
Level one thermagrapher (Snell Training)
www.thebuildingconsultant.com
www.parleebuilders.com
You build to code, code is the minimum to pass this test. Congratulations your grade is a D-
-
03-10-2010, 04:16 PM #9
Veteran Contributor
- Join Date
- Jul 2007
- Location
- Northern Jersey
- Posts
- 1,088
-
03-10-2010, 05:12 PM #10
Veteran Contributor
- Join Date
- Jul 2006
- Location
- Portland, OR
- Posts
- 2,316
Re: Brick Veneer Flashing
We had another thread here on the same thing, except without the brick ledge. All were flabergasted. It just seems to be SE tradition. Who knows how these things get started
The plastic in your detail serves no purpose, really, and the only drawback is absence of bonding between the bottom course of brick and the foundation. Bottom of the sheathing only gets wet if the WRB is short - and that's a WRB problem, not a plastic problem.
With a 2-brick ledge, all one needs to do is extend the WRB over the face of the back face of the ledge, and one is good.
If there is no brick ledge THEN one needs a good stick-on membrane and/or sheet metal flashing all around the base. That's how its done around here. We spend the money on metal, not on the concrete forming. Go figure
-
03-10-2010, 06:08 PM #11
Veteran Contributor
- Join Date
- Jul 2007
- Location
- Northern Jersey
- Posts
- 1,088
Re: Brick Veneer Flashing
I remember that thread NW but not the detail, I think its was Pete Engle who referred to the flashing detail as a "row lock" in where the brick is not bonded to the masonry cap. I still find that odd, according to that explanation the brick rested on a copper flashing with-in a mortar joint by gravity. That doesn't seems right to me.
Tom


Reply With Quote