Thread: Fiber Cement over old T1-11
-
12-30-2009, 07:15 PM #1
Regular Contributor
- Join Date
- May 2008
- Location
- Ridgefield, WA
- Posts
- 61
Fiber Cement over old T1-11
I have a client who wants me to install fiber cement over his existing T1-11. I'm concerned about rot issues that would come with this. I guess another contractor suggested just cutting the bottom off where its starting to swell and replacing that portion them just cover up. Is this a good Idea. Is there typically already a vapor barrier behind the T1-11, and would putting another layer of house wrap cause problems. Any advice is much appreciated.
jonny simons
-
12-30-2009, 08:22 PM #2
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Martinez, California
- Posts
- 14,198
Re: Fiber Cement over old T1-11
Jonny:
T1-11 was originally approved without a WRB behind it, only 4" strips were required behind the joints, better open it up and find out what's behind there."But one also finds in the human heart a depraved taste for equality, which impels the weak to want to bring the strong down to their level, and which reduces men to preferring equality in servitude to inequality in freedom"
― Alexis de Tocqueville "Democracy in America"
-
12-30-2009, 08:28 PM #3
Veteran Contributor
- Join Date
- Feb 2008
- Location
- North Central Vermont
- Posts
- 1,866
Re: Fiber Cement over old T1-11
Why? T-111 is no different than any plywood sheathing, except it typically has vertical grooves for better drainage.
Of course, remove any swollen or rotted section and replace with CDX.I guess another contractor suggested just cutting the bottom off where its starting to swell and replacing that portion them just cover up. Is this a good Idea.
If there's a vapor barrier, it would be on the inside behind the drywall. There won't be anything behind the T-111, so install housewrap over it and then siding.Is there typically already a vapor barrier behind the T1-11, and would putting another layer of house wrap cause problems.
Multiple layers of housewrap don't cause problems, since they are vapor permeable.Robert Riversong
Master HouseWright
-
12-30-2009, 09:58 PM #4
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Friday Harbor, San Juan Island, Washington
- Posts
- 13,029
Re: Fiber Cement over old T1-11
-
12-30-2009, 10:26 PM #5
Veteran Contributor
- Join Date
- Jan 2005
- Posts
- 9,061
Re: Fiber Cement over old T1-11
Yep - I got the OK from a manufacturer to double up WRB's before - no issues. Might look at a rain screen or at the very least a drain wrap.
“Racism is man's gravest threat to man - the maximum of hatred for a minimum of reason.”
Abraham J. Heschel (Jewish theologian and philosopher, 1907-1972)
-
12-31-2009, 07:53 AM #6
Veteran Contributor
- Join Date
- Jul 2004
- Location
- Western suburbs of Chicago
- Posts
- 5,554
Re: Fiber Cement over old T1-11
We've successfully gone over T-1-11 with other lap sidings in the past. I approach the job as if the T-1-11 is bare wall sheathing: I verify that its condition is good enough to hold nails & replace any questionable areas with new plywood. Then I repair or replace any damaged or missing flashings & install an appropriate WRB over the walls. Once this work is done, install your siding.
BTW - vapor barriers don't belong on the exterior of buildings in cold climates, as Robert has pointed out. Were you confusing the term with a weather resistant barrier (WRB) such as housewrap or felt paper?Greg
-
12-31-2009, 08:39 AM #7
Regular Contributor
- Join Date
- Jun 2007
- Location
- Redding, CA
- Posts
- 44
Re: Fiber Cement over old T1-11
I concur with gburnet. In numerous occurances, we have installed cement lap siding with success. We always remove the rotten and questionable areas.
In our area, a building permit is required with an inspection prior to house wrap(yes we always install new house wrap over the old siding). The inspector checks that the substrate being covered is not rotten and is structurally sound.
Experience has taught us to look for waves and other inconsistancies in the wall, especially on long walls. They get magnified when looking at the wall with new horizontal lines (lap siding). Shim them out if possible, similar to how a drywall hanger shims his boards out. But use felt paper shims instead of cardboard.
-
12-31-2009, 08:43 AM #8
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Des Moines, Iowa
- Posts
- 3,635
Re: Fiber Cement over old T1-11
Jonny
no more to add than what has been said; Go ForwardMark Parlee
EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
Level one thermagrapher (Snell Training)
www.thebuildingconsultant.com
www.parleebuilders.com
You build to code, code is the minimum to pass this test. Congratulations your grade is a D-
-
12-31-2009, 09:45 AM #9
Veteran Contributor
- Join Date
- Sep 2004
- Location
- down the shore
- Posts
- 2,031
Re: Fiber Cement over old T1-11
I'll second the notion of taking a look before you proceed. I've seen a number of different T1-11 installations. No wrb, felt over the studs behind the T1-11, a layer of celotex (fiberboard with a felt paper-like face) behind the T1-11. You get the idea. Best to look first.
-
01-01-2010, 01:18 AM #10
Regular Contributor
- Join Date
- May 2008
- Location
- Ridgefield, WA
- Posts
- 61
Re: Fiber Cement over old T1-11
Thank you for all your replies. It's good to know that you can double up on the WRB's (yes I was confusing terms).
Thank you also for the tip on checking for wavy walls, I don't imagine it was fun learning that one the hard way.jonny simons
-
01-01-2010, 01:46 AM #11
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Martinez, California
- Posts
- 14,198
Re: Fiber Cement over old T1-11
I wouldn't double up WRBs without checking first, people confuse water permeable, air permeable, and hydrostatic pressure permeable. The big factor is the water holdout time, if you've got a plastic wrap behind there no problem, if you've got asphalt impregnated felt paper or certain Kraft papers there could be a problem trapping water between the WRBs. check the attachment below, should you have a Two Ply super Jumbo Tex 60 Minute WRB you've got a 150-Minute Water Holdout time with a Vapor Permeability of 10 perms that will trap water, if you've got a 15 # asphalt felt you've got 20 minutes, a plastic wrap only 10 minutes with 50 perms, and a perforated plastic wrap virtually no water holdout or permeability. It won't take long to check and see what you have.
"But one also finds in the human heart a depraved taste for equality, which impels the weak to want to bring the strong down to their level, and which reduces men to preferring equality in servitude to inequality in freedom"
― Alexis de Tocqueville "Democracy in America"
-
01-01-2010, 02:04 AM #12
Veteran Contributor
- Join Date
- Feb 2008
- Location
- North Central Vermont
- Posts
- 1,866
Re: Fiber Cement over old T1-11
Since WRBs, by definition, are water impermeable and air impermeable, and not hydrostatic pressure impermeable, there should be no confusion (at least this side of the left coast).
No, the only pertinent factor is water vapor permeability.The big factor is the water holdout time
The building papers in your chart are for stucco cladding, are not applicable to other sidings, and are not what the IRC refers to as a WRB (which is #15 felt or equivalent). And even with stucco, it is recommended to install a double layer of grade D paper.Robert Riversong
Master HouseWright
-
01-01-2010, 03:47 AM #13
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Martinez, California
- Posts
- 14,198
Re: Fiber Cement over old T1-11
Jonny is located in Washington State, in all probability the building he is talking about was built under the UBC (the IRC didn't come out until 2000 and I don't know what date after that Washington adopted it), the UBC allowed either No. 15 asphalt rag felt or approved kraft paper, UBC §1402.1 in the 1997 UBC stated: "Such weather resistive barrier shall be equal to that provided for in UBC Standard 14-1 for kraft waterproof building paper or asphalt saturated rag felt." . The only applicable test at that time under the UBC was the "Boat Test" (water holdout) ASTM D779 based on Federal Specification UU-P-31b (incorporated into UU-B-790a). The Hydrostatic pressure Test specifically designed so polymeric materials could pass wasn't devised until later (they never were able to pass the Boat Test).
The fact is that if he has a WRB approved under the UBC it would comply with the Boat Test, unless the AHJ specifically approved a polymeric material under the alternate methods and materials code section, so the applicable standard would not be vapor permeability but water holdout. depending upon the age of the building there is a possibility that it has a plastic wrap, that's why I suggested that he check and see first, as I've said before T1-11 was originally approved with no WRB, just 4" strips behind the joints, if that's the case he has no problem, but that approved installation was not in the UBC and would had to have been approved by the AHJ under the alternate materials and methods section."But one also finds in the human heart a depraved taste for equality, which impels the weak to want to bring the strong down to their level, and which reduces men to preferring equality in servitude to inequality in freedom"
― Alexis de Tocqueville "Democracy in America"
-
01-01-2010, 11:25 AM #14
Veteran Contributor
- Join Date
- Feb 2008
- Location
- North Central Vermont
- Posts
- 1,866
Re: Fiber Cement over old T1-11
Which was a meaningless test, since WRBs are not intended to float on water without absorption, but to allow liquid water to drain vertically and vaporous water to permeate.
That test was adopted because it was more relevant to a weather barrier intended to resist wind-driven rain.The Hydrostatic pressure Test specifically designed so polymeric materials could pass wasn't devised until later (they never were able to pass the Boat Test).
The issue here was whether a double WRB would create a moisture problem, so the only relevant quality is permeance - whether the wall system can still breathe and dry.so the applicable standard would not be vapor permeability but water holdout.Robert Riversong
Master HouseWright
-
01-01-2010, 01:29 PM #15
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Martinez, California
- Posts
- 14,198
Re: Fiber Cement over old T1-11
Robert:
The function or a WRB is, as it's name implies, to make the structure weather resistant, that means to hold water out as long as possible while still allowing the structure to breathe. Water resistance and vapor permeability are two different issues, issues argued about ad infinitem by the differing industries manufacturing the different products.
Here is a good ASTM article on it by Tom Butt, FAIA, and a presentation by Tom.
California refused to approve plastic wraps for may years because they didn't hold-out water, here is a quote from one of DuPont's desperate attempts to get California to approve Tyvek:
Here a response of your fellow Vermonter, Martin Holladay, to a question on these fora in October of 2005:
Originally Posted by DuPont
Originally Posted by JLC Fora
¹ http://www.energy.ca.gov/title24/200...em_various.pdf
² http://forums.jlconline.com/forums/a...p/t-28288.html"But one also finds in the human heart a depraved taste for equality, which impels the weak to want to bring the strong down to their level, and which reduces men to preferring equality in servitude to inequality in freedom"
― Alexis de Tocqueville "Democracy in America"