    Replacing a number of lally columns in an 1870's farmhouse next month, and need opinions on the footings. I'm using 4" steel/cement lally columns, and from past jobs I pour rebar reinforced footings measuring 24x24x12.

    The client who has a relative in the masonry field, feels it's "extreme" and smaller footings measuring 12x12x6 would be ok. My philosophy has been to 'overbuild' things to exceed code and add a measure of safety.

    J

  2. #2
    Join Date
    Apr 2009
    Location
    midwestish
    Posts
    7,201

    Default Re: Footing Size for Lally Columns

    12x12x6 would be ok to hold that 4" pipe up in an interior application; does it need to help hold up the house too? If so, how much and what it's on, is more important than how old. The smaller size could be fine depending, the larger in most cases, would always work and add relatively little in added cost.

  3. #3
    Join Date
    Jun 2004
    Location
    Branford, CT 06405
    Posts
    3,652

    Default Re: Footing Size for Lally Columns

    There are two issues at play here, bearing size of the pad, and thickness of the pad.

    The 24x24 is 4x the bearing size of the 12x12, and very typically are specified for all sorts of pier installations.

    Who wants to say how much vertical force a 6" thick pad can handle before failing versus once again what could be considered the norm of the industry, 12" thick?

    Because we don't know what you are holding up, is the mason taking on the liability of specifying the foundation pier? Didn't think so!!!!

    Use the 24 x 24 setup!
    Take Care

    Jim

  4. #4
    Join Date
    Jun 2004
    Location
    Caldwell, NJ
    Posts
    3,153

    Default Re: Footing Size for Lally Columns

    Quote Originally Posted by Otis P. Driftwood View Post
    Replacing a number of lally columns in an 1870's farmhouse next month, and need opinions on the footings. I'm using 4" steel/cement lally columns, and from past jobs I pour rebar reinforced footings measuring 24x24x12.

    The client who has a relative in the masonry field, feels it's "extreme" and smaller footings measuring 12x12x6 would be ok. My philosophy has been to 'overbuild' things to exceed code and add a measure of safety.

    J
    Who says your overbuilding? Who cares what the relatives mason says also, he's not doing it. Screw him! Every footing around here is 24x24x12. Ask your inspector what you need. If he doesn't give you an answer go with what YOU want anyway.
    Joe Carola

  5. #5
    Join Date
    Sep 2005
    Location
    Washington, DC
    Posts
    4,683

    Default Re: Footing Size for Lally Columns

    Quote Originally Posted by MarkMc View Post
    12x12x6 would be ok to hold that 4" pipe up in an interior application;
    How can you make that statement w/o knowing what load the column is carrying? You can't.

    To the OP: You need to determine the load those columns will be carrying and the soil's bearing capacity to properly size the footings. It's too important a detail to guess. Pier footings that carry a concentrated load need to be thick. Slabs are poured 4-6 inches thick, and they get thickened to at least 12" where they carry a bearing wall, which is a line load, not concentrated.

    Spend some $$ and get those footings sized by an engineer.

    Tom
    1) Unconsciously Incompetent: He knows not, and knows not that he knows not. He is a fool. Shun him.
    2) Consciously Incompetent: He knows not, and knows that he knows not. He is simple. Teach him.
    3) Unconsciously Competent: He knows, and knows not that he knows. He is asleep. Wake him.
    4) Consciously Competent: He knows, and knows that he knows. He is wise. Follow him.

    May we all endeavor to progress from not knowing that we know not, to knowing that we know.

  6. #6
    Join Date
    Apr 2009
    Location
    midwestish
    Posts
    7,201

    Default Re: Footing Size for Lally Columns

    Quote Originally Posted by TSJHD1 View Post
    How can you make that statement w/o knowing what load the column is carrying? You can't.

    To the OP: You need to determine the load those columns will be carrying and the soil's bearing capacity to properly size the footings. It's too important a detail to guess. Pier footings that carry a concentrated load need to be thick. Slabs are poured 4-6 inches thick, and they get thickened to at least 12" where they carry a bearing wall, which is a line load, not concentrated.

    Spend some $$ and get those footings sized by an engineer.

    Tom
    Tom, read the full sentence..."does it need to help hold up the house too?".

    But you are correct, I can't, based on the info provided, and I didn't.

  7. #7
    Join Date
    Jul 2007
    Location
    Northern Jersey
    Posts
    1,283

    Default Re: Footing Size for Lally Columns

    UNLESS you pull apart the live and dead tributary loading of the that post there is no way anyone can help you. I would say 12" deep minimum and the 24 " x 24' is the way to go. ( say you have 1sqft of support for a bad soil type of 1200lbs /sf---doubling the size to 2x2 doesnt equal 2400lbs its 4 sqft x 1200 so 4800 lbs)Likely over done for most residential homes with a basic layout but we cant guess what your holding.
    Tom

  8. #8
    Join Date
    Sep 2005
    Location
    Washington, DC
    Posts
    4,683

    Default Re: Footing Size for Lally Columns

    Quote Originally Posted by MarkMc View Post
    Tom, read the full sentence..."does it need to help hold up the house too?".

    But you are correct, I can't, based on the info provided, and I didn't.
    I read the full sentence! But the way you wrote it completed the thought at the semicolon.

    Tom
    1) Unconsciously Incompetent: He knows not, and knows not that he knows not. He is a fool. Shun him.
    2) Consciously Incompetent: He knows not, and knows that he knows not. He is simple. Teach him.
    3) Unconsciously Competent: He knows, and knows not that he knows. He is asleep. Wake him.
    4) Consciously Competent: He knows, and knows that he knows. He is wise. Follow him.

    May we all endeavor to progress from not knowing that we know not, to knowing that we know.

  9. #9
    Join Date
    Apr 2009
    Location
    midwestish
    Posts
    7,201

    Default Re: Footing Size for Lally Columns

    Which was that the baby footing was big enough to hold the pipe - not a column or post, indoors and protected. Following the dotted comma it then went on to ask about the need for supporting the house.

    Give without remembering; take without forgetting.

  10. #10
    Join Date
    May 2005
    Location
    Truckee, CA
    Posts
    396

    Default Re: Footing Size for Lally Columns

    You need an engineer. Unless the client is an engineer, he has very little useful input. No professional would size footing by looking big enough.

  11. #11
    Join Date
    Jun 2004
    Posts
    581

    Default Re: Footing Size for Lally Columns

    One can look up the failure load of the lally column and compute the footing size from that.

    14000 pounds seems like reasonable failure load. About 7 square foot of footing. About 31"x31"x16".

  12. #12
    Join Date
    Aug 2006
    Location
    Leominster, MA
    Posts
    925

    Default Re: Footing Size for Lally Columns

    Quote Originally Posted by Joe Carola View Post
    Who says your overbuilding? Who cares what the relatives mason says also, he's not doing it. Screw him! Every footing around here is 24x24x12. Ask your inspector what you need. If he doesn't give you an answer go with what YOU want anyway.
    The BI agreed that the size of the footings (24x24x12) I spec'd out is the way to go, in spite of the client's "disagreement". Another case of a client looking to cut costs, which I'm seeing a lot of these days....

    Issue closed