Venting a bathroom vent through the attic and out the sloped roof
I'm looking for the newer thinking on this task because I've been thinking it anew and it's scheduled for this Friday.
Background facts: '80's single fam 2 1/2 story, whole house air, Panasonic 200 cfm vents (2 baths) on 2nd floor. Attic is fairly vented with new tab shingles, new ridge vent and scores of those 2" round soffit vents. And btw, the house sits on an unground spring and the roof sheathing is almost always wet on the underside in the winter. Two dehumidifiers run in the basement with springtime overflows. Bathrooms are mouldy and peely still, after I did the bath work 10 months ago. This new venting was planned to replace the 4" vinyl multi-bent hose to soffit.
This month I gave the roofers who put on the new roof, the Nutone black roof vent caps http://tinyurl.com/8hgt6k which they cut in. My job is connect the bath vents to the caps.
It seems the feds want an r-6 on vent pipes in attics. (Link) Aside from other moisture reducing tasks in the attic, my thought is to go 4" steel vent pipe, 3 screws, mastic, then wrapped with r-6 f.g. foil insulation. Why not a thermal bridge, say, 4" no-hub rubber coupling to break the heat/cold conduction? Why not pvc, maybe better?
Also, vent lit suggests a two foot long sweep coming out of the bath vent, to build up speed I guess. Does tight 90 cut that much? Distance from bath ceiling to roof, vertically, is about 4 feet.
Thoughts?
tia,
Victorian John
P.S. How do you guys copy a link to a text word that turns blue and we just click the word to bring up the link?Last edited by Victorian John; 12-31-2008 at 05:21 PM. Reason: P.S.
-
12-31-2008, 05:46 PM #2
Veteran Contributor
- Join Date
- Jan 2007
- Location
- Brooklyn, Fire Island
- Posts
- 5,326
Re: Venting a bathroom vent through the attic and out the sloped roof
you type
[ url = the web adress for the link ]
the word you want people to click on
[ / u r l ]
but without the spaces.
like thisFrancois
Truth is just one man's explanation for what he thinks he understands. (Walter Mosley)
-
12-31-2008, 09:34 PM #3
Veteran Contributor
- Join Date
- Feb 2008
- Location
- North Central Vermont
- Posts
- 1,866
Re: Venting a bathroom vent through the attic and out the sloped roof
You've got some serious moisture problems, and it's being excacerbated by poor roof venting.
A decent ridge vent has 18 square inches of net free vent area per foot, while a 2" button vent has 1.5 in², so balanced venting would require at least 6 button vents per foot of soffit (in other words, continuous) on each side of the roof to match the ridge. Insufficient intake vent allows the exhaust (ridge) vent to create a negative pressure in the attic, which will draw moist air through every crack and opening in the ceiling (wiring & plumbing penetrations, chimney opening, ceiling lights, attic hatch).
You need to seal the upstairs ceiling thoroughly, or you're going to rot your roof sheathing.
I would recommend either stainless steel or PVC duct. The PVC can have glued joints (best) and the ss should have something like foil/butyl tape at the connections. The smoother the pipe, the less pressure loss, and the plastic is less likely to condense than the metal.This new venting was planned to replace the 4" vinyl multi-bent hose to soffit...My job is connect the bath vents to the caps.
It seems the feds want an r-6 on vent pipes in attics. (Link) Aside from other moisture reducing tasks in the attic, my thought is to go 4" steel vent pipe, 3 screws, mastic, then wrapped with r-6 f.g. foil insulation. Why not a thermal bridge, say, 4" no-hub rubber coupling to break the heat/cold conduction? Why not pvc, maybe better?
Also, vent lit suggests a two foot long sweep coming out of the bath vent, to build up speed I guess. Does tight 90 cut that much? Distance from bath ceiling to roof, vertically, is about 4 feet.
A tight 90° elbow is the duct equivalent of 5' of straight, while a minimum 10" radius wide sweep is equivalent to 1½'. The wide sweep should have a straight leader between it and the fan that's twice the length of the duct size (8" for 4" duct) to reduce turbulence.
-
01-01-2009, 12:03 PM #4
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Des Moines, Iowa
- Posts
- 3,636
Re: Venting a bathroom vent through the attic and out the sloped roof
One of the vent styles I use is Pvc pipe on the top of the ceiling joist tilten down toward a gable end with the fan end a bit higher.
this allows any moisture to flow out and also allows the attic insulation to cover the pipe helping with any condensation issues. This of course does not work with a hip roof system.Mark Parlee
EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
Level one thermagrapher (Snell Training)
www.thebuildingconsultant.com
www.parleebuilders.com
You build to code, code is the minimum to pass this test. Congratulations your grade is a D-
-
01-02-2009, 05:18 PM #5
Veteran Contributor
- Join Date
- Jul 2008
- Location
- Suburbia (Washington, DC area)
- Posts
- 1,856
Re: Venting a bathroom vent through the attic and out the sloped roof
if the run is only 4', or even if it ends up at 7' with a bend or two, I would say just about anything will be fine in terms of air flow.
Where the condensed water goes is something to think about. It's not cold enough here that i've ever seen an issue on a bath vent, but YMMV.
I think Robert is right (as usual) that you have much bigger issues than the bath venting. If the sheathing is wet, there's stuff to fix on that house.
Doing good air sealing at the attic floor level (caulking topplates of all walls to the adjacent drywall, finding & sealing up accidental gaps, covering recessed lights, blocking up the tops of the baloon-framed walls & the plumbing wall that has no top plate, etc. etc., look up "air sealing" to find more info) is a good step.
Having said that, keeping the 'underground stream' out of the basement in the first place would solve the problem closer to its source. There are several approaches that can work; all are expensive; this house will have major problems until one of them is employed, if I understand your description correctly.Doug
Favorite tool this week: Duo-Fast HT550 hammer tacker
Blog:
Three types of gas tank hot water heaters for your renovation
-
01-04-2009, 04:40 PM #6
Veteran Contributor
- Join Date
- May 2005
- Location
- Boston
- Posts
- 245
Re: Venting a bathroom vent through the attic and out the sloped roof
Thanks Frenchie, Riversong, Mark and Doug. The job went well. It helped that Lowe's carried not only the lightweight 4" pipe, but also the light fittings including the 22 1/2 and street 45's and 90's. (3 bucks for a long sweep vs. 11 bucks for schedule 40).
The street ends fit the roof caps and Panasonic outputs perfectly.
BTW, my best buddy is a tech rep for air-handling industrial equipment, and it didn't dawn on me to ask him until you guys jogged my memory. Anyways, ASME standards are 5X the diameter for the straight out of the blower and equipment is tested and speced at that length. Turbulance and lambda don't ya know ;>
Thanks again. PVC, the only way to go. Not to choke on a knat, but vinyl-coated slinkies are soooo 70ish -;>
John
-
01-04-2009, 05:58 PM #7
Veteran Contributor
- Join Date
- Jul 2008
- Location
- Suburbia (Washington, DC area)
- Posts
- 1,856
Re: Venting a bathroom vent through the attic and out the sloped roof
Forgot to mention, anyway it's really just an afterthought for your job--I have stopped using through-roof vents wherever possible, having installed one that took on water 3x a year during our summer afternoon thunderstorm weather patterns. The water came right down the vent pipe and out the fan cover in the bath. Definitely something to consider depending on your weather, I decided gables & soffits make more sense.
Doug
Favorite tool this week: Duo-Fast HT550 hammer tacker
Blog:
Three types of gas tank hot water heaters for your renovation
-
01-04-2009, 09:07 PM #8
Veteran Contributor
- Join Date
- Feb 2005
- Location
- Gloucester MA
- Posts
- 244
Re: Venting a bathroom vent through the attic and out the sloped roof
Last edited by toobiloo; 01-04-2009 at 09:10 PM.
"I smell a lot of 'if' coming of this plan." -Jayne Cobb
-
01-04-2009, 09:16 PM #9
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Des Moines, Iowa
- Posts
- 3,636
Re: Venting a bathroom vent through the attic and out the sloped roof
schedule 20 is plenty
Mark Parlee
EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
Level one thermagrapher (Snell Training)
www.thebuildingconsultant.com
www.parleebuilders.com
You build to code, code is the minimum to pass this test. Congratulations your grade is a D-
-
01-04-2009, 09:43 PM #10
Veteran Contributor
- Join Date
- Feb 2008
- Location
- North Central Vermont
- Posts
- 1,866
-
01-04-2009, 09:48 PM #11
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Des Moines, Iowa
- Posts
- 3,636
Re: Venting a bathroom vent through the attic and out the sloped roof
Mark Parlee
EDI Certified EIFS Inspector/Moisture Analyst/Quality Control/Building Envelope II
Level one thermagrapher (Snell Training)
www.thebuildingconsultant.com
www.parleebuilders.com
You build to code, code is the minimum to pass this test. Congratulations your grade is a D-
-
01-04-2009, 09:51 PM #12
Veteran Contributor
- Join Date
- Feb 2005
- Location
- Gloucester MA
- Posts
- 244
Re: Venting a bathroom vent through the attic and out the sloped roof
Got it. Thanks to you both.
"I smell a lot of 'if' coming of this plan." -Jayne Cobb
-
01-05-2009, 03:51 AM #13
Veteran Contributor
- Join Date
- May 2005
- Location
- Boston
- Posts
- 245
Re: Venting a bathroom vent through the attic and out the sloped roof
Doug,
I think soffit vents are not allowed in some states such as CA. The idea being exhaled saturated air being picked up by the soffit vents and thrown back into the attic.
John
-
01-05-2009, 04:51 AM #14
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Portland, ME
- Posts
- 970
Re: Venting a bathroom vent through the attic and out the sloped roof
I was told the reason not to use PVC for dryer vents is that it will build up static electricity and clog up with lint. Anyone know if this is true?
Geoff
-
01-05-2009, 06:49 AM #15
Veteran Contributor
- Join Date
- May 2005
- Location
- Boston
- Posts
- 245
Re: Venting a bathroom vent through the attic and out the sloped roof
Butcher,
My buddy told me of a top 10 military-industrial company that tried to use pvc for a vacuum system on the assembly benches. The workers were getting zapped all the time. They had to rip it out.
For bath fans, saturated air is self grounding. I don't know about dryers though.
John