Thread: Bathroom extra outlets
-
10-31-2008, 04:12 PM #1
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,502
Bathroom extra outlets
I have a customer who wants a bidet/toilet combo unit, an unusual item I haven't done before. I have to put a new receptacle near the toilet. Here is the manufacturer's requirement:
Electrical service requirements – 120 VAC, 10A, 60Hz protected by Class A GFCI.
The unit is actually rated at about 600w. Is there a code provision that would prevent us from hooking it into the existing bath receptacle circuit? My sparky does not think we need a new home run and I can't find any pertinent provision in the code to contradict him.
Edit: the toilet/bidet is not direct-connect, it uses an ordinary cord and plug.Last edited by dgbldr; 10-31-2008 at 04:15 PM.
-
10-31-2008, 06:21 PM #2
Veteran Contributor
- Join Date
- Oct 2006
- Location
- Greensboro, NC
- Posts
- 1,383
Re: Bathroom extra outlets
I'm not a sparkey but even if the existing home run is 20 amp, you need 10 amps for the bidet, this only leaves 10 amps for a hair dryer etc.
Don't you put your customer at an inconvenience splitting the circuit that way ? They / you may wish that a new circuit was run.
-
10-31-2008, 07:36 PM #3
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,502
Re: Bathroom extra outlets
No, that's not an issue. Customer does not use hair dryers and would not be likely to dry both ends of his body at the same time anyway :)
This is strictly a code issue. I've left a message to the inspector, but I won't hear back till Monday and I need to plan the job this weekend.Last edited by dgbldr; 10-31-2008 at 07:40 PM.
-
10-31-2008, 07:46 PM #4
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Friday Harbor, San Juan Island, Washington
- Posts
- 13,029
Re: Bathroom extra outlets
You can get what, ~4000 watts out of a 20A circuit? I would not think a dedicated circuit would be needed unless there is a lot of lighting in the room. Do the instructions for the unit call for one?
-
10-31-2008, 07:58 PM #5
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,502
Re: Bathroom extra outlets
No, David, the only requirements by the manufacturer are stated in my OP: 120V, 10A GFI. As I said, strictly a code question.
Last edited by dgbldr; 10-31-2008 at 08:54 PM. Reason: typo
-
10-31-2008, 08:14 PM #6
Veteran Contributor
- Join Date
- Feb 2007
- Posts
- 403
-
10-31-2008, 08:15 PM #7
Veteran Contributor
- Join Date
- Feb 2007
- Posts
- 403
-
10-31-2008, 08:56 PM #8
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,502
Re: Bathroom extra outlets
Thanks Petey. I do know the dedicated bath circuit requirement, that's no problem here.
-
10-31-2008, 09:51 PM #9
Veteran Contributor
- Join Date
- Jun 2004
- Location
- Friday Harbor, San Juan Island, Washington
- Posts
- 13,029
-
10-31-2008, 11:34 PM #10
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,502
Re: Bathroom extra outlets
OK, how about this from IRC E3602.3:
"Fifteen- and 20-ampere branch circuits. A 15- or
20-ampere branch circuit shall be permitted to supply lighting units, or other utilization equipment, or a combination of both.
The rating of any one cord-and-plug-connected utilization
equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
The total rating of utilization equipment fastened in place, other than lighting fixtures, shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied."
Since my toilet is fastened in place, the last paragraph applies. So basically the 10A toilet on a 20A circuit is barely OK, but the same toilet cannot be added to a 15A circuit.
Correct?
-
11-01-2008, 03:12 PM #11
Veteran Contributor
- Join Date
- Feb 2005
- Location
- North Carolina
- Posts
- 2,240
-
11-05-2008, 06:15 AM #12
Veteran Contributor
- Join Date
- Aug 2005
- Location
- New Jersey
- Posts
- 315
Re: Bathroom extra outlets
Hi All,
Sorry to just drop in on the thread like this but what are the chances that the woman (and I feel comfortable assuming that it will be a woman) will be using the bidet and a hair dryer, curling iron or electric toothbrush at the same time ? I've had several instances where I've installed a receptacle off the load side of the bathroom GFI receptacle for items like this, a seat warmer or a towel warmer and there has never been an issue. As Petey mentioned, as long as the 20 amp circuit does not leave the bathroom and supply any other area it is acceptable.
-
11-05-2008, 07:46 PM #13
Veteran Contributor
- Join Date
- Dec 2005
- Location
- Michigan
- Posts
- 6,502
Re: Bathroom extra outlets
No it's not just a woman. In some cultures it is considered proper hygiene to wash after using the toilet, for both genders. That is the case here.
-
11-06-2008, 05:11 AM #14
Veteran Contributor
- Join Date
- Aug 2005
- Location
- New Jersey
- Posts
- 315
Re: Bathroom extra outlets
Thanks for the update but more information than we needed to know. Good luck with this.