Thread: Tandem or Single Pole Breaker
01-22-2008, 06:41 PM #1
- Jul 2004
- NYC
- 218
Besides having two for one, is there a difference between a tandem breaker and a single pole? Outside of being able to add more circuits to a load center, is there a reason to use a tandem breaker over a single?
-ML
01-22-2008, 07:30 PM #2
- May 2007
- Phoenix.AZ
- 154
Re: Tandem or Single Pole Breaker
""Besides having two for one, is there a difference between a tandem breaker and a single pole?""
Cost?
The full sized breaker would logically have more ability to dissipate heat.
01-22-2008, 07:36 PM #3
- 581
Both meet code. I prefer the half width breakers.
01-22-2008, 08:05 PM #4
- Aug 2005
- Nothern California
- 734
I think it is unlikely that AFCIs will come in tandem versions. So thinking about future circuit additions, it is better to have a full-width slots available for future AFCI use. So you're better off with a panel that gives you more full-width slots, rather than one that allows a bunch of tandems.
01-23-2008, 05:33 AM #5
- Aug 2005
- New Jersey
- 315
You're only permitted to have 42 circuits per panelboard. That being said most of the newer breaker panels that are made give you the ability to use tandem breakers but only in a given portion of the panel so that you cannot exceed 42 circuits. Thus, if you have an older 40 circuit breaker panel and begin using tandem breakers, technically speaking you can only use 2 tandem breakers. On the other hand, if you begin adding circuits and replace the std. breakers with tandems you will not only be in code violation but you will soon run out of neutral and ground bar space and run the risk of over-heating the panel. To make the blanket statement that tandem breakers are approved is not quite accurate. The panelboard has to be designed and approved to accept the tandems. If it weren't (and in theory) you could actually turn a 40 circuit panel into an 80 circuit panel.
01-23-2008, 09:47 AM #6
- Jul 2006
- Petersburg, Alaska
- 240
I prefer not to use tamdems except as a last resort. There is the heat disipating problem Alectrician mentioned and potential too many wires needed aplace to teminate in the panel mentioend by Goldstar. The one thing that has puzzeled me with tandems is do they count as 1 or 2 circuits when it comes to CTL rated panels? NEC states that a single pole counts as one and a 2-pole counts as two. Is a tandem considered a single or a double? Just food for thought
sparkyinak
"Good judgment comes from experience. Experience comes from poor judgment."
-unknown
01-23-2008, 10:32 AM #7
- 581
So much misinformation but that is to be expected.
They meet code. That is all that matters.
If you have problems with heat disipation or you put in more than a box is listed for, you have problems not the 1/2 width breakers.
01-23-2008, 12:54 PM #8
- Feb 2005
- North Carolina
- 2,240
I have wired many an apartment using 12/24 panels and mini breakers without any problems
01-23-2008, 01:30 PM #9
- 492
Tandem breakers are only allowed in number and slots that they are aproved for. Most 40 slot panels are only approved for 40 poles.
I am looking at a SQ QO load centers with main breakers rated at 200 amps.
They have 20 slot, 40 pole panel - 20 tandems
24 slot, 24 poles, no tandems allowed.
30 slots, 30 poles, no tandems allowed.
30 slots, 40 poles, 10 tandems allowed.
40 slots, 40 poles, no tandems allowed.
42 slots, 42 poles, no tandems allowed.
01-24-2008, 05:10 AM #10
- Aug 2005
- New Jersey
- 315
Bill,
You are 100% correct. The breaker panels that you cited are approved for use as described. In the case of the 30 breaker/40 circuit panel the bottom 5 slots are approved for tandem use (if desired) and thereby providing the means for making a 40 circuit panel.
Mike,
Using a 12/24 panel is OK if it is manufactured and approved for that use (but then again, you already knew that). You can probably land multiple EGC's on one terminal of the ground buss if it is marked for use in that manner. However, you can only land one neutral per terminal (but then again you already knew that also). You can also wire nut multiple EGC's and land a properly sized EGC to the terminal block providing you have the trough space inside the breaker cabinet for the splice. Can you also wire nut neutrals together and land one properly sized wire to the terminal bar ? (I'll bet you know the answer to that also). Just curious though, how did you end up with 24 circuits in an apartment ?
George,
Originally Posted by George Roberts
Making the blanket statement that "tandem breakers are approved" is not quite accurate. They are approved for use in certain panels and irrespective of whether that panel is designed for their use or not you cannot have more than 42 circuits per cabinet. Just as a side bar, can you install a multi-wire branch circuit (say a 14/3 RX cable using a common neutral) using a tandem breaker ?
Just to clarify, a two pole circuit breaker takes up two full breaker slots and provides circuit protection for two separate phases (240 volts in residential as an example). A tandem circuit breaker provides circuit protection for two single phase 120 volt circuits of the same phase. In some of the older panels there were two pole, tandem breakers (actually providing 4 separate s/p circuits) that were manufactured with approved handle ties. When you installed these breakers into the panel they took up two full circuit breaker spaces. Circuits 1 and 4 were one 2-pole, 240 volt circuit and circuits 2 and 3 were the other.
Originally Posted by sparkyinak
01-24-2008, 12:08 PM #11
- Oct 2005
- Florida
- 143
I'm no professional but I would say NO. Both breakers would be fed from the same bus and you would overload the neutral.Just as a side bar, can you install a multi-wire branch circuit (say a 14/3 RX cable using a common neutral) using a tandem breaker ?
01-24-2008, 01:53 PM #12
- Jul 2007
- SC
- 1
While not technically a tandem, the skinny (half height) breakers made by GE can be installed, in such a way in some GE panels, so that each is on a different hot leg, so yes, in certain cases , you can.can you install a multi-wire branch circuit (say a 14/3 RX cable using a common neutral) using a tandem breaker ?
01-24-2008, 08:12 PM #13
- Nov 2006
- Arizona
- 67
You can also do it with standard twins. You just cannot land both sides of a multiwire on the same twin. This comes in handy in a tight panel when you have multiple multiwire circuits, you just keep all your blacks on one leg and all your reds on the other, 2 of the same color per twin.
I am not too fond of twin quads however used on heavy loads such as HVAC. I have seen them melt down more times than I can count.
01-25-2008, 04:33 AM #14
- Aug 2005
- New Jersey
- 315
And...We have a winner !!!
Originally Posted by campster
Professional or not, knowing this much makes you more professional than many.
I'm glad you pointed that out. Next time you come across one see if they have an "HACR" label on the side.
Originally Posted by BigB56
01-25-2008, 12:13 PM #15
- Aug 2005
- 734