    1st time on this forum, don't beat me up!
    Jw Electric - great trucks- I seen them on rough carp forum.
    I'm a general constractor- My dads been wiring for me 19 years. Have a big remodel where we have a few places we need to add onto wires but would not like to put in a junction box. Local supply house- and inspector says they make nothing but I could swear I saw a new product this spring just for this that would pass inspection.
    Also, for stapling onto wood studs- do they make any good commercial staplers. His birthday is coming up.
    Thanks Rick

  2. #2
    Join Date
    Oct 2006
    Location
    Massachusetts
    Posts
    430

    Default Re: Splice behind wall

    Quote Originally Posted by zxsmurf View Post
    1st time on this forum, don't beat me up!
    Jw Electric - great trucks- I seen them on rough carp forum.
    I'm a general constractor- My dads been wiring for me 19 years. Have a big remodel where we have a few places we need to add onto wires but would not like to put in a junction box. Local supply house- and inspector says they make nothing but I could swear I saw a new product this spring just for this that would pass inspection.
    Also, for stapling onto wood studs- do they make any good commercial staplers. His birthday is coming up.
    Thanks Rick
    Never tried'em, but here you go:


    http://catalog.tycoelectronics.com/T...1394&LG=1&I=13

    The NEC reference is to manufactored buildings and such but I believe these or something similiar are approved for use wherever NM is approved.
    Last edited by edlee120; 10-13-2007 at 12:21 PM. Reason: clarity

  3. #3
    Join Date
    Feb 2005
    Location
    Ligonier Pennsylvania
    Posts
    123

    Default Re: Splice behind wall

    Thanks- That saved me alot of time- I think they were advertized in jlc magazine- Any thoughts on the stapler?

  4. #4
    Join Date
    Jul 2006
    Location
    Petersburg, Alaska
    Posts
    240

    Default Re: Splice behind wall

    Has any one used theses? I was doubtful at first but they check out. If used correctly, I'm sure it could cut material, labor, costs down. I'm just hesitent to radical new products. No track record to go on just the word of the manufacturer. Kind of like AFCI breakers.
    sparkyinak

    "Good judgment comes from experience. Experience comes from poor judgment."
    -unknown

  5. #5
    Join Date
    Feb 2005
    Location
    North Carolina
    Posts
    2,240

    Default Re: Splice behind wall

    Careful Gentelmen, look closely at the listing of these devices

    Product Facts
    Voltage rating: 300 VAC RMS
    Current rating: 20 amperes
    Meets requirements of National Electrical Code, Articles 545, 550, 551

    Also let's look at the NEC

    300.15 Boxes, Conduit Bodies, or Fittings — Where Required.
    Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (M).

    (F) Fitting. A fitting identified for the use shall be permitted in lieu of a box or conduit body where conductors are not spliced or terminated within the fitting. The fitting shall be accessible after installation.

    Yes you can use one of these but it must be accessible meaning that it can't be behind a finished wall.
    Seeking to be the best and the safest in the electrical trade.

  6. #6
    Join Date
    Feb 2007
    Posts
    403

    Default Re: Splice behind wall

    Quote Originally Posted by jwelectric View Post
    Meets requirements of National Electrical Code, Articles 545, 550, 551
    I read that too. No mention of Art. 300 or 334.

  7. #7
    Join Date
    Jun 2004
    Location
    Meadow Vista, CA
    Posts
    2,108

    Default Re: Splice behind wall


  8. #8
    Join Date
    Jul 2006
    Location
    Petersburg, Alaska
    Posts
    240

    Default Re: Splice behind wall

    I saw that too. If you read the listing it was tested under, it states that it meets the requirements of 334.

    Tyco listing:
    http://database.ul.com/cgi-bin/XYV/t...589&sequence=1

    QAAV.GuideInfo Nonmetallic-sheathed Cable Interconnectors:

    http://database.ul.com/cgi-bin/XYV/t...589&sequence=1

    Outline of Investigation for Nonmetallic Sheathed Cable Interconnectors:

    http://ulstandardsinfonet.ul.com/outscope/2256.html

    If you this link, it mentions Article 336 which the article for NM when this requirement was written (2001)

    The web site the link is from is not a website that would be frequented by residential sparkies. If you dig into the products you will see that at least the ones I read, they are can be used as the NEC applies which allows interconnectors 334.30(C)
    sparkyinak

    "Good judgment comes from experience. Experience comes from poor judgment."
    -unknown

  9. #9
    Join Date
    Feb 2005
    Location
    North Carolina
    Posts
    2,240

    Default Re: Splice behind wall

    Yes this device can be used on NM cable and I am not disputing this.

    It can be used on NM cable when as outlined in their listing and labeling which is only for mobile units as outlined in the link of the original post.

    For a stick built house the code sections I have posted would rule the installation. The only sections that will allow the Splices and Tap device to be canceled are 545, 550, 551.

    If this device is used in a stick built house then the device will be required to be accessible.
    Seeking to be the best and the safest in the electrical trade.

  10. #10
    Join Date
    Jul 2006
    Location
    Petersburg, Alaska
    Posts
    240

    Default Re: Splice behind wall

    JW, I agree
    sparkyinak

    "Good judgment comes from experience. Experience comes from poor judgment."
    -unknown

  11. #11
    Join Date
    Feb 2007
    Posts
    403

    Default Re: Splice behind wall

    It would seem that 334.40(B) directly allows this. I'm not sure if that tap is what is being described there.
    Thing is 300.15(F) takes away any allowance given in 334.40