NOTICE: Thank you for your continued patience with the persistent bugs affecting the JLC Online Forums. We've setup a special email address for reporting issues and defects. Reports will go directly to the assigned IT team members. Please include screenshots if you can. There were some widespread issues over the past weekend which have been resolved. However, we know that various error pop-ups are still occurring during post composition and at other times. Thanks again. Here's the email address:
See more
See less

Vent the dryer in 2x4 wall

  • Filter
  • Time
  • Show
Clear All
new posts

  • Vent the dryer in 2x4 wall

    What products are available to get a dryer vent built in a 2x4 wall (new construction) and piped down through the bottom wall plate? It is an interior wall over an outside soffit below, and we can frame so the plate has no beams or joists immediately below the subfloor.

    I see the "dryer box" product made for a 2x4 wall, but its duct opening is oval. Typical dryer vent duct, flexible or not, is 4" diameter.

  • #2
    Re: Vent the dryer in 2x4 wall


    We typically transition from 4" round to a 3" x 6" rectangular duct inside the wall, and back to 4" again to exit through the jack. This is a simple custom detail. You have a few options aside from this, but the important thing is to keep the cubic inch volume the same or slightly larger when you transition between each type of duct, and to keep the bends and length to a minimum.



    • #3
      Re: Vent the dryer in 2x4 wall

      Gene -

      We use the Dryer Box product with an oval-to round-transition. Steve at Dryer Box may have these oval-to-round transitions to sell to you, or you can get them from your local H.V.A.C. supplier.