NOTICE: Thank you for your continued patience with the persistent bugs affecting the JLC Online Forums. We've setup a special email address for reporting issues and defects. Reports will go directly to the assigned IT team members. Please include screenshots if you can. There were some widespread issues over the past weekend which have been resolved. However, we know that various error pop-ups are still occurring during post composition and at other times. Thanks again. Here's the email address:
See more
See less

One hour fire rated exterior wall

  • Filter
  • Time
  • Show
Clear All
new posts

  • One hour fire rated exterior wall

    OK. Need a little help here. Frustration at dangerous level and rising..
    Many times in the past I have drawn/specified and had approved the following as a 1hr. fire rated wall.

    5/8X finish, 2x4 studs 16"o.c., db. top pl., sgl. bot. pl., 3&1/2 FG batts, 1/2" osb/ply'd sheathing with 3&5/8" thk. brick veneer ext. finish.
    Now the new plan checker wants me to indicate a specific assembly listed in the IRC table 720.1 or a UL approved assembly. for a one hour wall.
    There are dozens in the IRC but none exactly like this and only about a gadzillon UL listed assemblies that would take days to search through.

    Anyone have any idea where I might get this information. Thanks

  • #2
    Re: One hour fire rated exterior wall

    I'm not familiar with the IRC but around here they are always requiring 5/8" DensGlass on the exterior for sheathing. The Fire rating assemblies are provided by the manufacturer and should be in that link.
    You will ask what goal the U.S. is pursuing? .... their external debt is huge, and ruining other countries is their customary method. Even ownership of the global 'printing press' is no longer helping. Nor is full control over NATO, None of that if enough for the 21st century colonizers. They don't just need to preserve the dollar as the only global currency but also to get their hands on the economic wealth of other large powers and regions. - Sergei Naryshkin


    • #3
      Re: One hour fire rated exterior wall

      Try UL #U305.

      1) Unconsciously Incompetent: He knows not, and knows not that he knows not. He is a fool. Shun him.
      2) Consciously Incompetent: He knows not, and knows that he knows not. He is simple. Teach him.
      3) Unconsciously Competent: He knows, and knows not that he knows. He is asleep. Wake him.
      4) Consciously Competent: He knows, and knows that he knows. He is wise. Follow him.

      May we all endeavor to progress from not knowing that we know not, to knowing that we know.


      • #4
        Re: One hour fire rated exterior wall

        The reason they are asking for a reference number is because you are using a variable/uncontrollable material as one of the layers. The veneer brick at first glance would seem to be a fire-rated material, however, most materials used in these assemblies are independently rated materials having already had their properties tested and analyzed.

        A typical one-hour wall, as shown in U305, is the start point for achieving a rated wall when required at say closer than 3' to the property line or a one-hour rated exterior wall bearing assembly. OK, there are also interior one-hour rated walls, but in this case, the brick veneer tells me its probably exterior.
        Take Care



        • #5
          Re: One hour fire rated exterior wall

          James. Thanks. You are right. I was trying to make the brick veneer as part of the assembly. That's why I couldn't find it anywhere. Actually I have a one hour assembly without the brick veneer. It is item #15-1.15 in the 2003 IRC, table 702.1(2) which we are still using.
          I have to consider the 1 hr. rating from the inside only since I'm more than 5' from prop. line.


          • #6
            Re: One hour fire rated exterior wall

            I have the IRC2003, both the standard book, and the Connecticut amended versions, and I do not find item 15-1.15 in Table 702.1(2). That table is in the IWall Covering Section of the codebook.

            Now I can find Item 15-1.15 in the IBC2003, page 120, however, that is a 2 hr 2x6 wall assembly.

            What happens is although the base codes are the same, different states adopt different versions, then they amend them for specifics. For example, we use the 2005 CTSBC, Connecticut State Building Code, which is the base IRC2003 "amended" to create our 2005 code. Gets to be a pain sometimes, especially if you work across state lines.

            Anyway, you get the drift of the assembly and how it works; it's pretty difficult to change a part, and keep the assembly rating!
            Take Care



            • #7
              Re: One hour fire rated exterior wall

              James you are right again. I had read the D**m things so many times that I was seeing double. I have know idea what I was thinking.
              However, I did find what I needed. I think?
              "American Wood Council/American Forest & Paper Assoc". ASTM E 119 / NFPA 251
              Thanks for the help.


              • #8
                Re: One hour fire rated exterior wall

                According to the Fort Worth Building Codes website, the current version of the Commercial Building Code for that jurisdiction is the 2009 IBC (with local amendments) and commercial structural designs are typically required to be prepared by a design professional.


                See Section 107.1

                It appears you're not even using the correct Code (IBC not IRC) or Code Cycle (2009 not 2003)

                You will likely do best to have a professional designer handle this submittal for you.

                The designer will know what to provide and save you all the wasted time and frustration not knowing where to begin.

                Good Luck.


                • #9
                  Re: One hour fire rated exterior wall

                  UL listings for fire rated assemblies actually do make sense once you've decoded the systems and their applications. This table helps tremendously:

                  NFPA-80A ( is also noteworthy if we are talking about exterior protectives.